Tony suggested that I start a forum thread on my problem so here goes.
The last two smokes I have been having trouble with getting the temp up. With the Auber set at 247 and the smoker set to 250 I couldn't get to 235 on the Auber temp sensor. My Thermoworks thermocouple agreed with the Auber.
On the next smoke, I set the Auber to 225 and the smoker set at 250. I watched the Auber temp go up to 216 and then drop to 208 with the out light on the Auber on and the light on the smoker off. After a while the light on the smoker came back on. As a test, I turned the smoker temp knob down slowly. The smoker clicked when I passed 240 and the smoker light went out. The Auber temp read 208. The temp sensor in the smoker is clean.
Here is more trouble shooting:
1. Yes, The temp knob was all the way up.
2. I just ran the smoker without the Auber and with the temp knob set to full, 250. For a load I put a pan of water on the bottom shelf. I recorded temps with two thermocouple junctions inside. One was hanging about 2 inches from the ceiling and the other was about 6 inches from the ceiling of the smoker. I didn't keep track of which sensor was which. The graph from the thermocouple recorder is posted as an attachment. Here is what I see on the graph.
It looks like the on-board temp controller kicks out at about 250 but does not kick back in until the temp drops to about 220. If I have the Auber in series with the on-board controller and the Auber set at a temp above 220, I can get into a situation where the Auber is calling for power and the on-board controller is switched off. That must really confuse the logic in the Auber.
3. I am using a drop in Auber probe.
4. I drop and fasten the probe so that it is just above the meat but not touching it.
5. Before my first smoke, I auto tuned with a pan of wet sand for a load. I dropped the temp sensor to a place just to the side of the load.
I suppose I could bypass the on-board controller but then the smoker is not safe to plug in if the Auber is not in the circuit.
The last two smokes I have been having trouble with getting the temp up. With the Auber set at 247 and the smoker set to 250 I couldn't get to 235 on the Auber temp sensor. My Thermoworks thermocouple agreed with the Auber.
On the next smoke, I set the Auber to 225 and the smoker set at 250. I watched the Auber temp go up to 216 and then drop to 208 with the out light on the Auber on and the light on the smoker off. After a while the light on the smoker came back on. As a test, I turned the smoker temp knob down slowly. The smoker clicked when I passed 240 and the smoker light went out. The Auber temp read 208. The temp sensor in the smoker is clean.
Here is more trouble shooting:
1. Yes, The temp knob was all the way up.
2. I just ran the smoker without the Auber and with the temp knob set to full, 250. For a load I put a pan of water on the bottom shelf. I recorded temps with two thermocouple junctions inside. One was hanging about 2 inches from the ceiling and the other was about 6 inches from the ceiling of the smoker. I didn't keep track of which sensor was which. The graph from the thermocouple recorder is posted as an attachment. Here is what I see on the graph.
It looks like the on-board temp controller kicks out at about 250 but does not kick back in until the temp drops to about 220. If I have the Auber in series with the on-board controller and the Auber set at a temp above 220, I can get into a situation where the Auber is calling for power and the on-board controller is switched off. That must really confuse the logic in the Auber.
3. I am using a drop in Auber probe.
4. I drop and fasten the probe so that it is just above the meat but not touching it.
5. Before my first smoke, I auto tuned with a pan of wet sand for a load. I dropped the temp sensor to a place just to the side of the load.
I suppose I could bypass the on-board controller but then the smoker is not safe to plug in if the Auber is not in the circuit.